Daikin Air Conditioner Ductless Mini-Split (FTXS / FDXS / FTXM / RMXS) F3 Error Code

What the F3 code means

F3 is discharge pipe temperature control: the compressor's discharge pipe thermistor has exceeded its threshold and the control has stopped the compressor to protect it (service manual SiUS091133). The thresholds are class-dependent — stop temperatures run from about 99-110°C on the 09/12 class up to 120°C on the 24/30/36 class, clearing several degrees lower. A discharge that hot means the compressor is working against a starved or mis-metered refrigerant circuit — or that the thermistor reporting it is lying. Daikin's flow therefore starts with the thermistors, then the expansion valve, then the refrigerant line itself.

Likely causes

  1. Defective discharge pipe thermistor (or outdoor heat exchanger / outdoor air thermistors skewing the reading)
  2. Defective electronic expansion valve or coil
  3. Refrigerant shortage
  4. Defective four-way valve
  5. Water mixed in the refrigerant
  6. Defective stop valve
  7. Defective outdoor unit PCB

How to fix it — step by step

  1. Confirm F3 with the remote self-diagnosis. The unit has already protected itself — the compressor stopped on temperature — so do not defeat the pause by rapid restarts
  2. Breaker off. Daikin's flow starts with the thermistors (Check No. 01): confirm the discharge pipe thermistor is connected and test the thermistors against the resistance chart — a discharge thermistor reading falsely high produces exactly this code with a healthy system, and a genuinely failed one is replaced → Shop the discharge pipe thermistor at Amazon
  3. Next in the documented order: Check No. 12, the electronic expansion valve and its coil — a valve that under-feeds the outdoor coil starves refrigerant flow and overheats the discharge
  4. Then Check No. 14, the refrigerant line: shortage (leak), water mixed in the refrigerant, the four-way valve, and the stop valves — sealed-system checks with gauges
  5. If thermistors, expansion valve and refrigerant line all pass, the documented remainder is the outdoor unit PCB
  6. Measure the discharge pipe thermistor against Daikin's Check No. 01 chart (disconnect its connector from the PCB and measure the sensor itself): 20 kOhm at 25 C, about 25 kOhm at 20 C, 16.1 kOhm at 30 C, 10.6 kOhm at 40 C and 7.2 kOhm at 50 C (R25 = 20 kOhm, B = 3950 K). A reading far off the chart for the pipe's actual temperature condemns the thermistor; a sensor clipped off the pipe or with a damaged harness reads the air instead of the pipe and produces the same false trip.
  7. Hand a shop this pinpoint: F3 confirmed, the discharge thermistor's resistance reading if taken, and the class thresholds for your size (the stop temperatures run 99-120°C by class) — that tells the technician whether the trip was marginal or extreme

Did that fix it?

Worked through the steps? Say where you landed - it pinpoints what to do next.

Parts that commonly fix the F3 code

Typical pro repair $450–$2,000

Typical ranges, checked Nov 2026. Your model’s exact part can land outside them.

Before you buy: check the discharge pipe thermistor first

Test: Disconnect the thermistor's connector from the PCB and measure its resistance at the sensor's actual temperature (Daikin service manual SiUS091133, Check No. 01).

A good one reads: About 20 kΩ at 25 °C (77 °F); 25 kΩ at 20 °C; 16.1 kΩ at 30 °C; 65.9 kΩ at 0 °C; 10.6 kΩ at 40 °C. Open, shorted or far off the chart means the thermistor has failed.

Test values from manualshelf.com documentation - confirm against your model's own tech sheet.

What fixed yours?

Fixed this on your machine? Tap what did it - reports from owners set the percentages on this page.

Source: manufacturer / repair documentation. Codes can vary by model — confirm against your manual.