Daikin Air Conditioner Ductless Mini-Split (FTXS / FDXS / FTXM / RMXS) F6 Error Code
What the F6 code means
F6 is high pressure control in cooling. On the FTXS/FDXS LV pair — which carries no physical high-pressure switch — this thermistor-based control is how high pressure protection is implemented, doing the job that E3 does on switch-equipped models. SM-TS3 gives the underlying condition plainly: 'abnormal high pressure or refrigerant overcharged.' The control stops the compressor before pressure can damage it; the code therefore reports a condition (heat rejection failing or too much refrigerant), not a single part.
Likely causes
- Abnormally high pressure in cooling (dirty outdoor coil, blocked airflow, overcharge)
- Refrigerant overcharged (SM-TS3's wording)
- Defective thermistor skewing the control's pressure estimate
How to fix it — step by step
- Confirm F6 with the remote self-diagnosis, then do the documented external check first: breaker off, clean the outdoor heat exchanger and clear airflow obstructions around the outdoor unit — a heat-choked outdoor coil is the most common driver of high pressure in cooling
- Run cooling under load and see whether F6 returns with a clean coil and clear airflow
- If it returns, the remaining documented cause is refrigerant-side: SM-TS3 names abnormal high pressure or refrigerant overcharged — a system that was recently charged and now trips F6 was likely overcharged, and correcting the charge is sealed-system work with gauges and a scale
- Hand a shop the pinpoint: F6 confirmed, coil cleaned, and whether the system was recently serviced or recharged — that history usually decides this code
Did that fix it?
Worked through the steps? Say where you landed - it pinpoints what to do next.
Good - you're done. If it comes back, the causes at the top of this page are where to look first.
This fault usually needs a technician - but this is the part they would test first.
Then the likely broken part is the outdoor unit PCB.
Parts that commonly fix the F6 code
- outdoor unit PCB$80–$400Shop at Amazon
Typical ranges, checked Nov 2026. Your model’s exact part can land outside them.
What fixed yours?
Fixed this on your machine? Tap what did it - reports from owners set the percentages on this page.
Source: manufacturer / repair documentation. Codes can vary by model — confirm against your manual.