Peerless Boiler Pinnacle (PI / PI-T) series, PI25 control F00 Error Code
What the F00 code means
A fault lockout: high limit exceeded. The boiler overheated and locked out, and the red fault light is on until the S4 reset key clears it after the cause is fixed. The manual's causes run wider than flow alone: a shorted thermostat circuit or a failed water pressure switch can also produce this lockout.
Likely causes
- Circulation pump not operating correctly
- Inadequate flow, with more than a 50 degree F rise from return to supply
- Thermostat circuit short or stray voltage where gray thermostat wires are used
- High limit switch faulty, tripping below its temperature
- Water pressure switch or its wiring harness faulty
How to fix it — step by step
- Record the code, F00, before pressing reset, and read supply temperature on the LED display and the status menu.
- Safety: if overheating occurs or the gas fails to shut off, shut off the gas at the service valve. Do not cut power to the circulating pump, which can aggravate overheating.
- Locate the circulator, the high limit switch and the water pressure switch, and check circulation first by confirming less than a 50 degree F rise from return thermistor to supply thermistor in the status menu.
- Test: if the supply temperature reads below 210 degrees F while F00 is set, the high limit switch is tripping early and is faulty. Temporarily jumping out the water pressure switch and finding F00 can then be reset condemns that switch or its harness. Where gray thermostat wires are used, disconnecting and jumping them together and finding the code resets cleanly proves a thermostat circuit short or stray voltage. → Shop the water pressure switch at Amazon → Shop the high limit switch at Amazon
- End at the fix: restore circulation and flow, replace a high limit switch that trips below 210 degrees F, replace a water pressure switch proven bad by the jumper test, and repair the thermostat circuit if the wire test isolated it there. Press S4 reset and observe a full firing cycle.
Did that fix it?
Worked through the steps? Say where you landed - it pinpoints what to do next.
Good - you're done. If it comes back, the causes at the top of this page are where to look first.
This fault usually needs a technician - but this is the part they would test first.
Then the likely broken part is the High limit switch.
Shop the High limit switch at Amazon
Also tied to this fault: Water pressure switch - Shop at Amazon; Circulator - Shop at Amazon
Parts that commonly fix the F00 code
- High limit switchShop at Amazon
- Water pressure switch$50–$205Shop at Amazon
- CirculatorShop at Amazon
Typical ranges, checked Nov 2026. Your model’s exact part can land outside them.
What fixed yours?
Fixed this on your machine? Tap what did it - reports from owners set the percentages on this page.
Source: manufacturer / repair documentation. Codes can vary by model — confirm against your manual.
Manual & model number
Find your model number on the rating plate on the boiler jacket, often behind the front panel. It's the key to the right manual pages and the right parts.